Turn on suggestions
Showing results for
06-04-2010 06:30 AM
Hello,
On our DCX switches with 8Gb SFP+ transceivers, sfpshow indicates max cable length of 20m with 62.5u cables (OM1/M6) and 50m with 50u cables (OM2/M5). On 4100/4900 switches with 4Gb SFPs, sfpshow indicates max length of 70m with 62.5u and 150m with 50u cables.
This is all in agreement with the Brocade document "Cabling_Best_Practices_GA-BP-036-02.pdf".
My question is what is the max cable length supported with 8Gb SFP+ transceivers when the port speed is set to 4Gb with a 50u (OM1/M6) cable? Does it behave like a 4Gb SFP and allow a max cable length of 150m? I presume it does but would appreciate confirmation from the experts.
Thanks,
Alastair
06-04-2010 06:47 AM
--->>> Does it behave like a 4Gb SFP and allow a max cable length of 150m?
Yes. See table below.
Meters | 1Gb | 2Gb | 4Gb | 8Gb | 10Gb |
SM | 10km | 10km | 10km | 10km | 10km |
OM3 | 500m | 300m | 380m | 135m | 300m |
OM2 50.0 | 500m | 300m | 150m | 50m | 82m |
OM1 62.5 | 300m | 150m | 70m | 21m | 33m |
If you are satisfied with the responses please mark as 'Answered'.
If not, just let me know I can see to get more info.
I would appreciated if you rate the threads.
Thank You.
06-04-2010 07:20 AM
Thanks for the speedy reply!