Sent: May 21, 2026 02:00 AM
From: Matic Lulik
Subject: NSX Upgrade from 4.2.1.3 - NSX Managers become unresponsive
Hi all,
When we upgraded second location we first did 2 workarounds mentioned above on hosts that are hosting EDGE NODES:
We had no issues during upgrade.
Original Message:
Sent: Apr 15, 2026 06:24 AM
From: Matic Lulik
Subject: NSX Upgrade from 4.2.1.3 - NSX Managers become unresponsive
Hi Serhii,
Happy to share more details to help the community avoid this "perfect storm."
Our environment is quite dense, which I believe was the main trigger. We have around 20 Edge Clusters (approx. 40 Edge Nodes total), and in our design, we can have a maximum of 30 Edge Nodes per ESXi host during maintenance or failover scenarios.
Here are the specifics that led to the XMAP exhaustion:
Edge Node Size: Large
vNIC Configuration: Each Edge Node has 2 vNICs (Management is on a separate vSwitch, so only 2 vNICs are requesting XMAP on the vDS)
The "Math" behind the crash: Support clarified that with a Ring Size of 2048, each vNIC requests a memory region of exactly 425,805,440 bytes (~400 MB) in the XMAP table.
With 2 vNICs per Edge, that's 800 MB per Node.
With 30 Nodes on a single host, the requirement is ~24 GB just for the Edges.
Add the NSX Managers, other infrastructure VMs, and the kernel bug (where regions don't overlap correctly), and you quickly exceed the default 32 GB XMAP limit.
The Bug: A known issue in the kernel prevents these memory regions from overlapping/sharing correctly. During the upgrade, as vNICs are detached and re-attached, "zombie" entries or lack of overlapping caused the XMAP table to hit the limit.
Management Impact: This is why our NSX Managers lost connectivity. When they migrated to a host that was already "XMAP-starved" by the Edge Nodes, the kernel couldn't allocate the required memory region for the Manager's vNIC, resulting in the MAC 00:00:00:00:00 state.
Current Action Plan: We are implementing the workaround (64 GB XMAP and 32 P2M buffers) exclusively on the hosts that are designated to host Edge Nodes. We don't see a need to apply this to the general compute clusters at this time.
If you have high-density Edge placements or use the 2048 Ring Size, I would strongly recommend checking your XMAP usage before triggering the upgrade.
Best regards, Matic
Original Message:
Sent: Apr 14, 2026 05:20 AM
From: Serhii
Subject: NSX Upgrade from 4.2.1.3 - NSX Managers become unresponsive
Hi Matic,
Thank you for sharing your experience and the response from Broadcom support.
Could you please share more details about your environment, such as the number of VMs per host, the presence of "monster" VMs, the number of VMs with more than 2–3 vNICs, the number and size of your Edge nodes, and whether you are using Enhanced Data Path (EDP) (and in which mode)?
This would help us better understand the issue and assess whether it could potentially occur in our infrastructure. Based on the KB, it is unclear in which specific environments this issue can be reproduced.
Thank you.